Default Question for you electricians....

My wife wants to connect a refrigerator in our basement. Problem is, that there's not an electrical outlet nearby. She wants me to get an extension cord and run that to the nearest outlet. I'm trying to tell her that's not a good idea and I should acutally try to run another outlet from the nearest.

Who's right here?

Secondly, can I simply run another oulet from the nearest one? Does a refrigerator require a separate dedicated-type line? The refrigerator plug is a simple 3 prong.

I re-did some of the wiring in the basement a few years ago and think that the line I want to tap into now has 1 PC, 2 printers, a scanner and 2-3 lights on it.

Opinions please.

Thanks
Len
Old 03-12-2003, 11:17 AM
  #2  
VegasJen
CFOT Attention Whore

Support Corvetteforum!
 
VegasJen's Avatar
 
Member Since: Dec 2001
Location: Press "2" for English
Posts: 48,714
Received 79 Likes on 32 Posts

Default Re: Question for you electricians.... (1970 Stingray)

well, it certainly wouldn't be to code. i've seen it done in some places. i wouldn't do it if i didn't have to but it might be the best option for you. how far do you have to go? i would try to keep the cord to a minimum, even cutting off excess cord and putting a new plug end on it. use the larger gauge cord, like the orange industrial cords most of us have in our garages for using those big, halogen lights. then if it makes you feel better, and it would me, i'd replace the recepticle your going to use with a GFIC recepticle to give you a little protection. then the only problem will be knowing when the recepticle pops before everything melts.
and to answer your question, of course your right. :thumbs:
Old 03-12-2003, 11:54 AM
  #3  
joe73vette
Melting Slicks
 
joe73vette's Avatar
 
Member Since: Dec 2000
Location: Eastern Connecticut
Posts: 2,198
Likes: 0
Received 2 Likes on 2 Posts
Default Re: Question for you electricians.... (clutchdust)

The electrical code requires a seperate circuit for refrigerators. It also doesn't like lights and outlets on the same circuit. Both rules are to prevent problems when the outlet circuit trips, so you are stuck not in the dark with spoiling food. If you are capable of running a new outlet, do it. Better yet, run a new circuit back to the panel. They make half width CBs so you can have two circuits where there was once one. Joe
Old 03-12-2003, 12:02 PM
  #4  
Teuffelhunde
Burning Brakes
 
Teuffelhunde's Avatar
 
Member Since: Oct 2002
Location: death to the southeast
Posts: 813
Likes: 0
Received 0 Likes on 0 Posts
Default Re: Question for you electricians.... (joe73vette)

I'd just run a new outlet from a nearby outlet. Just wire it in paralel to the old circuit and there won't be any problems, electrically. I myself wouldn't be the least bit concerned about building codes but other people might.
Old 03-12-2003, 12:34 PM
  #5  
VegasJen
CFOT Attention Whore

Support Corvetteforum!
 
VegasJen's Avatar
 
Member Since: Dec 2001
Location: Press "2" for English
Posts: 48,714
Received 79 Likes on 32 Posts

Default Re: Question for you electricians.... (1970 Stingray)

i'd agree with joe, that is certainly the correct and best way to do this. ultimately however, the questions you have to ask yourself are, "am i going to sell this refrigerator with the house?, how long will this be like this? and how much money and time do i want to spend?" if the answers are 'no', '>a few years' and 'not a lot' then do it the easy way but you'll run the risk of popping a circuit breaker or GFI and having the frige thaw. your choice.
are you lucky enough to have a circuit breaker panel in that basement? if so, that would be really easy and preferable.
Old 03-12-2003, 12:51 PM
  #6  
LAvetteman
Safety Car
 
LAvetteman's Avatar
 
Member Since: Jan 2001
Location: South Central Louisiana
Posts: 4,659
Received 3 Likes on 3 Posts
St. Jude Contributor

Default Re: Question for you electricians.... (clutchdust)

What ever cord or wire you use make sure it is at least 14 awg (gauge).

Running a fridge and the other small items you mentioned on one circuit as you mentioned shouldn't be a problem. Just make sure you dont plug any heavy hitters in the same circuit. (heater, microwave, A/C, hair dryer, vacuum.
Old 03-12-2003, 01:14 PM
  #7  
hauk
Instructor
 
hauk's Avatar
 
Member Since: Feb 2003
Location: jacksonville florida
Posts: 176
Likes: 0
Received 0 Likes on 0 Posts
Default Re: Question for you electricians.... (clutchdust)

I am a retired electrician,The NEC (National Electrical Code)Requires a seperate circuit for the frig,However you could tap it into another circuit as long as you make sure of the amperage draw on that circuit.# 14 wire is good for 15 amps,If you are going to run an extention cord very far use #12 AWG,That will take care of the voltage drop(if you have a lot of voltage drop caused by too much load on a circuit or too long a cord you could burn the refrigerator compressor up).
Old 03-12-2003, 06:36 PM
  #8  
Jughead
Senior Member since 1492
Support Corvetteforum!
Thread Starter
 
Jughead's Avatar
 
Member Since: Aug 2000
Location: Just because I'm paranoid doesn't mean people aren't out to get me...
Posts: 86,382
Received 152 Likes on 118 Posts
St. Jude Donor '09

Default Re: Question for you electricians.... (hauk)

Thanks for the info guys. :thumbs: Just as I expected.....I was right(I think). I'm gonna run another outlet from the nearest one in an adjacent wall....right now there's only a rarely used extra laundry workshop lamp plugged into that one. Distance about 16 total feet away.

I'm gonna scrap my wife's extension cord idea. :yesnod:

Thanks again, the C3 forum always comes thru for me regardless the question. :yesnod: :thumbs: :hurray: :hurray:


[Modified by 1970 Stingray, 6:37 PM 3/12/2003]
Old 03-12-2003, 06:43 PM
  #9  
stpman
Melting Slicks
 
stpman's Avatar
 
Member Since: Oct 2002
Location: I may be getting old but I refuse to grow up
Posts: 2,865
Received 1 Like on 1 Post

Default Re: Question for you electricians.... (1970 Stingray)

if it is a regular sizes fridge the best option is to run a new outlet from the breaker box. the problem with connecting to an outlet nearby is unless you wired the outlet how do you know what is connected to that outlet, I've seen houses where the was half of the house wired to one 15 amp circuit! The thing that some overlook is it is not just a building/electrical code concern but an insurance issue as well. in some areas if wiring is done and not inspected you may have trouble with your house insurance should there be a problem.

Steve
Old 03-12-2003, 07:30 PM
  #10  
Clink69
Drifting
 
Clink69's Avatar
 
Member Since: Sep 2000
Location: Germantown Maryland
Posts: 1,355
Likes: 0
Received 0 Likes on 0 Posts
Default Re: Question for you electricians.... (1970 Stingray)

I was an electrician.. code calls for 20 AMP in kitchen seperate circuit. Basement fridge , probably 15 amps is OK. But again it depends on the Fridge, if its a big one the surge current will be an issue. Don't run extension cords... Mixing lights and plugs is a :nono: also do not use a GFI...
Old 03-12-2003, 07:47 PM
  #11  
ndirishr1
Burning Brakes
 
ndirishr1's Avatar
 
Member Since: Aug 2002
Location: Indianapolis Indiana
Posts: 1,077
Received 2 Likes on 1 Post

Default Re: Question for you electricians.... (1970 Stingray)

I'm a safety manager. Run the outlet. Extension cords have started a lot of home fires.
Old 03-12-2003, 10:16 PM
  #12  
CWUin82
Burning Brakes
 
CWUin82's Avatar
 
Member Since: Sep 1999
Posts: 773
Likes: 0
Received 0 Likes on 0 Posts

Default Re: Question for you electricians.... (1970 Stingray)

15 amp circuit, 14awg is fine as long as it is a dedicated line for the fridge. If you are going to run a seperate circuit, may as well use a 12 gauge wireand make it a 20 amp circuit.
Extention cords are fine as long as your smoke detectors are in working order.
Old 03-13-2003, 12:47 AM
  #13  
jackson
Le Mans Master

 
jackson's Avatar
 
Member Since: Sep 2001
Location: Unreconstructed, South Carolina
Posts: 7,739
Received 628 Likes on 556 Posts

Default Re: Question for you electricians.... (1970 Stingray)

Thanks for the info guys. Just as I expected.....I was right(I think). I'm gonna run another outlet from the nearest one in an adjacent wall....right now there's only a rarely used extra laundry workshop lamp plugged into that one. Distance about 16 total feet away. I'm gonna scrap my wife's extension cord idea. Thanks again, the C3 forum always comes thru for me regardless the question. [Modified by 1970 Stingray, 6:37 PM 3/12/2003]
Len:
I like that approach ... especially if that circuit breaker & wiring is sufficient for fridge's startup surge. I've seen computers do funny things when on same circuit as fridge ... unless there's a ups or line conditioner at pc the big surges when comp starts aren't good for pc. Many years ago I was an electrician in southern cal ... commercial-industrial w/ a bit of residential on the side ... but I sure don't remember code. BTW ... how's your BBC project?
Jack


Old 03-13-2003, 12:54 AM
  #14  
boredsoIstrokedit
Racer
 
boredsoIstrokedit's Avatar
 
Member Since: Jun 2001
Location: Sanford Florida
Posts: 440
Likes: 0
Received 0 Likes on 0 Posts
Default Re: Question for you electricians.... (1970 Stingray)

Whatever way you go (I would wire in a new outlet if it is in an unfinished basement) make sure you use 12 guage wire, and make sure the circut has a GFI in it. Good luck. :cheers:
Old 03-13-2003, 08:54 AM
  #15  
wayne_69_427
Pro
 
wayne_69_427's Avatar
 
Member Since: Sep 2002
Location: High Point, NC
Posts: 599
Received 0 Likes on 0 Posts

Default Re: Question for you electricians.... (1970 Stingray)

Tell your wife that when the house burns down the insurance will not pay because electrical was not done to code. :thumbs: :thumbs: :thumbs:
Old 03-13-2003, 12:46 PM
  #16  
carl a
Safety Car
 
carl a's Avatar
 
Member Since: Jun 2002
Posts: 4,135
Likes: 0
Received 1 Like on 1 Post

Default Re: Question for you electricians.... (1970 Stingray)

your right -ive seen cords burn-actually on fire -the breaker trips on overload or short -- if you got a cheapo 16 guage cord and your pullin 19 amps the cord will burn before the breaker trips- thats why theres fires when people plug in electric space heaters using cheapo extension cords- a normal kitchen usually gets 2- 20 amp appliance feeds-(for the counter top outlets) the fridge is on one of these-just open the 1900 box pull 2 wires-a hot and a neutral-(dont need a ground if you use mettalic conduit) and youll be fine-- you check the amount of current being drawn using a ampprobe-- depending on whats on thats circut--- if the lights ect are on one circut and the washer then youll blow then the compressor kicks on- then you gotta take the hot back to the panel and put her on a breaker-#12 wire for 20 amp feed--- hope this helps-carl-24s yrs local 134 chicago-- chicago has the toughest codes and there not one for a dedicated line in the kitchen for the fridge


[Modified by carl a, 5:51 PM 3/13/2003]
Old 03-13-2003, 12:51 PM
  #17  
carl a
Safety Car
 
carl a's Avatar
 
Member Since: Jun 2002
Posts: 4,135
Likes: 0
Received 1 Like on 1 Post

Default Re: Question for you electricians.... (1970 Stingray)

your right -ive seen cords burn-actually on fire -the breaker trips on overload or short -- if you got a cheapo 16 guage cord and your pullin 19 amps the cord will burn before the breaker trips- thats why theres fires when people plug in electric space heaters using cheapo extension cords- a normal kitchen usually gets 2- 20 amp appliance feeds-(for the counter top outlets) the fridge is on one of these-just open the 1900 box pull 2 wires-a hot and a neutral-(dont need a ground if you use mettalic conduit) and youll be fine-- you check the amount of current being drawn using a ampprobe-- depending on whats on thats circut--- if the lights ect are on one circut and the washer then youll blow then the compressor kicks on- then you gotta take the hot back to the panel and put her on a breaker-#12 wire for 20 amp feed--- hope this helps-carl-24s yrs local 134 chicago

Get notified of new replies