How many amps is the breaker for your four post lift?

Thread Tools
 
Search this Thread
 
Old 04-19-2009, 09:15 PM
  #1  
my 76 ray
Melting Slicks
Thread Starter
 
my 76 ray's Avatar
 
Member Since: Mar 2007
Location: Hinckley OH
Posts: 2,520
Likes: 0
Received 10 Likes on 4 Posts

Default How many amps is the breaker for your four post lift?

I am in the market for a four post lift. All the makers tell you the volts of the motor (120 vs 240) but none of their sites tell you how many amps are needed. So can you guys please tell me how many amps the breaker has for the circuit you use for your lift, the volts for your motor (can you wire your motor for 120 or 240) and the brand and model (if you know it) of your lift?

I want to make sure I have enough juice to run the lift I buy without adding wiring.

Thanks

Chuck
Old 04-19-2009, 09:32 PM
  #2  
Gordonm
Race Director
 
Gordonm's Avatar
 
Member Since: Dec 1999
Location: Forked River NJ
Posts: 19,593
Received 754 Likes on 464 Posts

Default

My 2 poster is a 240 volt motor. I ran a double pole 30 amp breaker. I ran 12/2 wiring. The motor is a 2 HP and pulls 19 amps at max power.
Old 04-19-2009, 10:12 PM
  #3  
Dave J
Burning Brakes
 
Dave J's Avatar
 
Member Since: Jul 2006
Location: Deplorableville Nebraska
Posts: 1,225
Received 137 Likes on 107 Posts

Default

I have a 4 post, Autolifters I bought used (hardly) 220 volt. Listed amperage is 19.5, and the motor is rated at 3 HP. The previous owner installed a long power cord, and I just plug it into the dryer outlet just inside the house from the garage. The wife hasn't complained yet...
Old 04-19-2009, 10:40 PM
  #4  
my 76 ray
Melting Slicks
Thread Starter
 
my 76 ray's Avatar
 
Member Since: Mar 2007
Location: Hinckley OH
Posts: 2,520
Likes: 0
Received 10 Likes on 4 Posts

Default

Originally Posted by Gordonm
My 2 poster is a 240 volt motor. I ran a double pole 30 amp breaker. I ran 12/2 wiring. The motor is a 2 HP and pulls 19 amps at max power.
What brand is your lift?
Old 04-20-2009, 01:41 AM
  #5  
Frogday
Drifting
 
Frogday's Avatar
 
Member Since: Jul 2002
Location: Woodinville WA
Posts: 1,697
Likes: 0
Received 3 Likes on 2 Posts

Default

I am about to add two 4-post lifts and am wondering how many amps they pull at 120v. I'm not in any rush to raise the cars, they are just being stacked for storage, so 120v is all I need.
Old 04-20-2009, 02:52 AM
  #6  
TimAT
Le Mans Master
 
TimAT's Avatar
 
Member Since: Oct 2006
Location: Gladstone MO
Posts: 7,121
Received 424 Likes on 385 Posts
C3 of Year Finalist (appearance mods) 2019

Default

Good rule of thumb is a 120v motor will draw twice the current of the same HP motor on 240v. If it draws 19.5 amps on 240 it'll need 40 amps on 120v.
Old 04-20-2009, 06:35 AM
  #7  
Gordonm
Race Director
 
Gordonm's Avatar
 
Member Since: Dec 1999
Location: Forked River NJ
Posts: 19,593
Received 754 Likes on 464 Posts

Default

Originally Posted by my 76 ray
What brand is your lift?
Mine is a Direct lift purchased from Greg Smith equipment. www.gregsmithequipment.com

I agree on the 120 volt. They pull twice as many amps as a 240 volt. I don't care how fast or slow you want it. Check the motor rating it will tell you the amps. 240 is not hard at all to wire up
Old 04-20-2009, 07:03 AM
  #8  
Lotadoh
Instructor
 
Lotadoh's Avatar
 
Member Since: Apr 2005
Location: Finksburg Maryland
Posts: 200
Likes: 0
Received 0 Likes on 0 Posts

Default

Just some general electrical information. You should only load a breaker to 80%, so if the lift is drawing 19.5 amps, you should use a 30 amp breaker with #10 wire. #12 wire is only good for 20 amps, and should only be protected with a 20 amp breaker.
Old 04-20-2009, 08:41 AM
  #9  
crossfire1982
Advanced
 
crossfire1982's Avatar
 
Member Since: Dec 2007
Location: Cramerton NC
Posts: 83
Likes: 0
Received 2 Likes on 2 Posts

Default

Im running my Eagle 4 post lift on a 120 volt 15 amp ground fault circuit with no problems at all.
Old 04-20-2009, 09:59 AM
  #10  
ahphares
Instructor
 
ahphares's Avatar
 
Member Since: Sep 2001
Location: bay city mi
Posts: 153
Likes: 0
Received 1 Like on 1 Post

Default

Ditto. I have been running my Direct-Lift for 4 years on 120V, 15amp, grd-fault circuit with absolutely no problems. Motor/pump combo seems to run free with no real load noticeable. Using a short light duty extension cord to the wall and cord stays cool to the touch.

Andy
Old 04-20-2009, 07:39 PM
  #11  
my 76 ray
Melting Slicks
Thread Starter
 
my 76 ray's Avatar
 
Member Since: Mar 2007
Location: Hinckley OH
Posts: 2,520
Likes: 0
Received 10 Likes on 4 Posts

Default

Originally Posted by TimAT
Good rule of thumb is a 120v motor will draw twice the current of the same HP motor on 240v. If it draws 19.5 amps on 240 it'll need 40 amps on 120v.
Are you sure that's correct? I thought it will still draw only 19.5 amps, however, when run on 120 v it gets all 19.5 amps on one power wire. When run on 240 v it splits the amps between the two power wires, therefore, it uses 9.75 amps per power wire.

At least that's the way I understood it when I converted my air compressor from 120 to 240. It sure made a difference when it was cold in the garage.
Old 04-20-2009, 07:53 PM
  #12  
Gordonm
Race Director
 
Gordonm's Avatar
 
Member Since: Dec 1999
Location: Forked River NJ
Posts: 19,593
Received 754 Likes on 464 Posts

Default

Originally Posted by my 76 ray
Are you sure that's correct? I thought it will still draw only 19.5 amps, however, when run on 120 v it gets all 19.5 amps on one power wire. When run on 240 v it splits the amps between the two power wires, therefore, it uses 9.75 amps per power wire.

At least that's the way I understood it when I converted my air compressor from 120 to 240. It sure made a difference when it was cold in the garage.
No electrician here but I did stay at a Holiday Inn last night. I think you are half right. Using a double pole breaker on a 240 volt I thought the 19 amps was split in two so you had 9.5 amps on each.

If you are running it on 120 volts the amps will double to 38 and you would need a 50 amp breaker to be safe and bigger wire.
Old 04-20-2009, 08:15 PM
  #13  
mikep3
Burning Brakes
 
mikep3's Avatar
 
Member Since: Dec 2005
Location: Baldwinsville, NY
Posts: 992
Received 55 Likes on 37 Posts

Default Electrical Power

I looked at several lift mfg. web sites, 4 post storage, 4 post lifts, 2 post lifts.
Most did not list the complete motor specs. HP, Amps, Voltage.
some were 1 HP, 1.5HP, 2HP and 3HP, I would think that 1HP & 1.5HP could be run on 120/208/220 volt, but the 2, 3 & 5 HP units would need 220 volt due to the amps.
Most electrical tech books list that.

Figure about 1400 watts per horsepower.
Divide Watts by volts to get Amps, for example:
•3hp motor, 120V
•3hp X 1400 W = 4200 W
•4200 W / 120 V = 35 A
Old 04-20-2009, 09:38 PM
  #14  
Lotadoh
Instructor
 
Lotadoh's Avatar
 
Member Since: Apr 2005
Location: Finksburg Maryland
Posts: 200
Likes: 0
Received 0 Likes on 0 Posts

Default

I am an electrician. With any piece of equipment, the wattage it draws always stays the same, no matter what voltage it is hooked to. The higher the voltage, the lower the amp draw. Any equipment hooked up 240, will draw half the amps of equipment hooked to 120. If the lift can be hooked up 120 or 240, it should also tell you the amp draw at both voltages. One advantage of hooking it up 240, is that you can run smaller wire and use a smaller breaker. Just remember that you don't want an oversized breaker. It needs to match the wire you run, to protect the wire.. 15 amp for #14 20 amp for #12 30 amp for #10
Old 04-21-2009, 07:14 AM
  #15  
Gordonm
Race Director
 
Gordonm's Avatar
 
Member Since: Dec 1999
Location: Forked River NJ
Posts: 19,593
Received 754 Likes on 464 Posts

Default

Originally Posted by Lotadoh
I am an electrician. With any piece of equipment, the wattage it draws always stays the same, no matter what voltage it is hooked to. The higher the voltage, the lower the amp draw. Any equipment hooked up 240, will draw half the amps of equipment hooked to 120. If the lift can be hooked up 120 or 240, it should also tell you the amp draw at both voltages. One advantage of hooking it up 240, is that you can run smaller wire and use a smaller breaker. Just remember that you don't want an oversized breaker. It needs to match the wire you run, to protect the wire.. 15 amp for #14 20 amp for #12 30 amp for #10
After reading your response I went out and checked. I was going off memory before, not a good thing. I did run #12 wire and a double pole 20 amp breaker for my lift. The run is quite short as the lift is within 6 feet of the circuit box. Was I correct in the amps being split by running a double pole 20 amp breaker for a motor that peaks at 19 Amps for 240 volts?
Old 04-21-2009, 07:19 PM
  #16  
Lotadoh
Instructor
 
Lotadoh's Avatar
 
Member Since: Apr 2005
Location: Finksburg Maryland
Posts: 200
Likes: 0
Received 0 Likes on 0 Posts

Default

At 19 amps 240 volt, you should basically see 19 amps on each pole (phase) of the breaker. At 120 volts, you would see 38 amps on a single pole breaker. Generally you wouldn't load a breaker to more than 80% of its rating, so with a 19 amp load, a 30 amp breaker with #10 wire would be ideal, but a lift doesn't run continuously, so a 2 pole 20 amp breaker with #12 wire, will work fine for this application. Basically, the circuit breaker is not for equipment protection. Its protection against the wires burning up.Thats why the breaker amp rating should never be larger(there are exceptions) than the amp rating of the wire.The lift motor should have built in protection. Hopefully that helps.
Old 04-21-2009, 08:34 PM
  #17  
Gordonm
Race Director
 
Gordonm's Avatar
 
Member Since: Dec 1999
Location: Forked River NJ
Posts: 19,593
Received 754 Likes on 464 Posts

Default

Yes that helps. As I recall I asked specifically what amp and wire I should use and went with their recomendation. It runs a maximum of 45 seconds at a time.

Get notified of new replies

To How many amps is the breaker for your four post lift?

Old 04-22-2009, 07:11 PM
  #18  
CCrane65
Safety Car

 
CCrane65's Avatar
 
Member Since: Apr 2000
Location: Wichita KS
Posts: 3,768
Received 48 Likes on 27 Posts

Default

I bought a 110v lift from Greg Smith Equipment and it's on a 20 amp circuit.

cc
Old 04-22-2009, 08:36 PM
  #19  
my 76 ray
Melting Slicks
Thread Starter
 
my 76 ray's Avatar
 
Member Since: Mar 2007
Location: Hinckley OH
Posts: 2,520
Likes: 0
Received 10 Likes on 4 Posts

Default

Originally Posted by CCrane72
I bought a 110v lift from Greg Smith Equipment and it's on a 20 amp circuit.

cc
Is that the Direct-Lift? And are you happy with it? It's one that I'm considering.
Old 04-22-2009, 09:10 PM
  #20  
400hp427vette
Melting Slicks
 
400hp427vette's Avatar
 
Member Since: Mar 2008
Location: North Bellmore Ny
Posts: 2,336
Likes: 0
Received 1 Like on 1 Post
St. Jude Donor '09
Default

Originally Posted by Lotadoh
Just some general electrical information. You should only load a breaker to 80%, so if the lift is drawing 19.5 amps, you should use a 30 amp breaker with #10 wire. #12 wire is only good for 20 amps, and should only be protected with a 20 amp breaker.

An 80% rated breaker means that after 3 hours there will be enough heat to cause a bi-metallic breaker to trip at 80% load. So in the case of a lift that would only run a few minutes at a time going over 80% load would be fine. One thing to think about is circuit protection is really product protection.