OT Air Compressor Question
https://www.tractorsupply.com/tsc/pr...r?cm_vc=-10005
https://www.tractorsupply.com/tsc/pr...mpressor?rfk=1
Last edited by elwood13; Jun 8, 2018 at 10:39 PM. Reason: pictures show in edit but not on post





If you are talking about pumping up tires or using an impact wrench or blowing debris off parts, then a small compressor should suffice. If you are planning to run a sand blaster or paint gun all day, then get the larger one. I have a small contractor compressor (like one used for nail guns) that I use all the time for probably 90% of the jobs in my shop. It only has a small tank, but it pumps up to 120 PSI in less than 30 seconds. My big compressor is an 80 gallon IR that I use for sand blasting and painting.
Charles





https://www.corvetteforum.com/forums...ete-floor.html
I just bought the 60-gallon version this morning and will leave it on the pallet, and will cut up an old tire and make some rubber pads to go between the pallet and the concrete floor.
I plan to make some marks on the floor, and if it shows any signs of walking around, I will anchor it.
The Best of Corvette for Corvette Enthusiasts
Last edited by Robert61; Jun 9, 2018 at 06:45 PM.
couple of links for info.
http://weldingweb.com/showthread.php...gnetic-starter
https://www.garagejournal.com/forum/...ad.php?t=87388
I have a twin stage 80 gal compressor like the IR. It draws 22 amps running. The 30 amp breaker should be fine for the big twin stage 220v compressor. Keep in mind that the breaker should be sized to protect the equipment and wiring. A 25 amp would probably be better to protect the motor, but your compressor motor will come with a thermal overload to protect it and your wire is good for the 30 amp. Never put in a breaker larger than the capacity of the wire, especially for the house wiring in the wall.
Your wire is 3 conductor #10 awg SO cord. It should be good for 30 amps depending on the length. See http://www.usawire-cable.com/pdfs/nec%20ampacities.pdf for NEC capacities. The 3 conductor cord should have 4 wires, red, white, and black with a smaller green wire for the equipment ground. You need to check the wiring diagram for the compressor to see if you need the equipment ground, I recommend it as a safety concern.
The cord caps, ends on the cord are only 20 amp and should not be used with a 22 amp draw. You have to look at the wiring diagram to see what you need. I ran 10/3 with ground to my compressor, but I cannot remember if the safety ground was needed.
I have had both a 60 gal single stage and the 80 gal twin stage. I highly recommend the twin stage for air tools and painting if you are using a 1/2" impact and various air sanders. You don't have to wait for it to catch up. It works well with sand blasting the the higher pressure.
Air hose is cheap and it won't fry something or someone if it is cut. Your 220v extention cords will be a tripping hazard and possible electrical hazard. I would put the air compressor in a more or less permanent position and buy 50' or more of 3/8" hose. The extension cord length may be limited due to increased current (amp draw) of the wire. It is a PIA moving a vertical tank compressor around safely.
Just my $.02.
Last edited by R66; Jun 11, 2018 at 05:25 AM. Reason: breaker
I have a small 3hp, 20 gallon, Campbell Hausfeld compressor that I have used around my garage for about 30 years. Shortly after getting it, I was using it to drive a pneumatic buffer. After about 30 minutes of almost continuous use I could actually smell it in the shop. It had gotten very warm.
I realized then, I could not use it for more than 30 minutes without a cooling down period.Later I mentioned this to my AmsOil distributor when picking up some oil for my diesel pickup (15 qts!), and he mentioned that they actually made a synthetic oil specifically for compressors. I decided to give it a try. A while later I was using the compressor to drive the high cfm buffer again and after about 45 minutes realized that I couldn't smell the compressor so decided to go check on it. When I got within a few feet I could tell it was warm, but it was running just fine and was not overheating as before. I don't believe it will make your compressor something it's not, but I am convinced it will make it live longer... regardless of how you typically use your compressor.
Good luck... GUSTO